  1. Updating the V1.2 PipLite cards with firmware V1.1 solved this problem. Shame about the lack of helpful posts in a week though!
  2. The following applies to a networked installation of 300+ CTS amplifiers. We have a design file which was written to control CTS amplifiers with V1.1 PipLite cards. We have had about 10 replacement PipLite cards for failed items, however these cards have been supplied as PipLite V1.2. Given that there are numerous (25+) control objects per card in the design file, can you advise if there is a way to globally update these objects without having to re-write the software?! You assistance in this matter is very much appreciated.